4-wire system for unbalanced loads

A four-wire system is suitable to supply unbalanced, three-phase loads or single phase loads distributed on all three phases of a low voltage installation.

Power Measurement On Four-Wire System
Power Measurement On Four-Wire System (on photo: Measuring power with Metrel's device MI 3102 Eurotest XE; credit: itrservis.ru)

When measuring power on a three-phase system, it is really necessary to take into consideration the fact that the three-phase power supply system might not be balanced (pointers of phase to phase voltages UL1/L2, UL2/L3 and UL3/L1 taken in sequence do not form an equilateral triangle).

Problem comes due to powerful unbalanced three phase loads connected to the mains installation.

Let’s discuss now about three-phase and single-phase wattmeter methods //


1. Three-phase wattmeter method

Principle of power measurement on three-phase four-wire system using three-phase wattmeter
Figure 1 – Principle of power measurement on three-phase four-wire system using three-phase wattmeter

Three-phase wattmeter measures all three-phase voltages, phase currents and delays between the voltages and currents. On this basis it can calculate the three power levels separately for each phase, as well as the level of the total three-phase system.

Power measurement on three-phase four-wire system, using the measuring device
Figure 2 – Power measurement on three-phase four-wire system, using the measuring device

All three power levels can be read out directly on the display of metering device. This method enables power measurement on all three phases simultaneously and is particularly suitable for unbalanced power. In the case of balanced power, one wattmeter can be used and moved to all three phases in three steps.


2. Single-phase wattmeter method

Where there are nonsymmetrical three-phase loads or single-phase loads usually connected to four-wire system, it is necessary to measure power on all three phases (it is not possible to measure one phase only and calculate the power of total three-phase system).

Measurement, using the measuring device runs in three steps, where each step is equal to the measurement on a single-phase system.

First step //

Power measurement on three-phase system (first step)
Figure 3 – Power measurement on three-phase system (first step)

Result 1 P1 = U1 × I1 × cos φ1 (active power)

Result 2 Q1 = U1 × I1 × sin φ1 (reactivepower)

Result 3 PA1 = U1 × I1 (apparent power)


Second step //

Power measurement on three-phase system (second step)
Figure 4 – Power measurement on three-phase system (second step)

Result 1 P2 = U2 × I2× cos φ2………(active power)


Third step //

Power measurement on three-phase system (third step)
Figure 5 – Power measurement on three-phase system (third step)

Result 1 P3 = U3 × I3× cos φ3 (active power)

Result 2 Q3 = U× I3 × sin φ3 (reactivepower)

Result 3 PA3 = U3 × I3 (apparent power)

In each step the instrument measures phase voltage, phase current and delay between the voltage and current.

On the basis the of measured results for each phase, we can calculate all three total powers of three-phase system according to the following equations //

Ptot = P1 + P2 + P3 (total active power of three-phase system)

Qtot = Q1 + Q2 + Q3 (total reactive power of three-phase system)

PAtot = √(Ptot2 + Qtot2) (total apparent power of three-phase system)

PFtot = Ptot / PAtot (power factor)

Reference // Measurements on electric Installations in theory and practice – Instruction manual by Metrel

SEARCH: Articles, software & guides

Premium Membership

Premium membership gives you an access to specialized technical articles and extra premium content (electrical guides and software).
Get Premium Now ⚡

About Author

author-pic

Edvard Csanyi

Electrical engineer, programmer and founder of EEP. Highly specialized for design of LV high power busbar trunking (<6300A) in power substations, buildings and industry fascilities. Designing of LV/MV switchgears.Professional in AutoCAD programming and web-design.Present on

One Comment


  1. Dr.R.Jayapal
    Apr 09, 2016

    I am an Electrical engineer with 40 years of experience in power plant design,Automation, Teaching etc. This site is simple and useful to power engineers. I am doing freelance consulting now. If you can use me, it will be mutually beneficial. Thanks.
    Dr.R.Jayapal,
    Coimbatore,India
    Ph: +91 9994687310

Leave a Comment

Tell us what you're thinking... we care about your opinion!

Premium Membership

Get access to premium electrical guides, technical articles and much more!