Residual currents (earth fault)

The measurement of the earth fault or residual currents on a distribution system feeder can be done by the so-called summation connection, where the three current transformers, one in every phase, are connected and the summated current is brought to the inputs of an earth fault protection relay.

Measurement of residual currents on a distribution feeder
Measurement of residual currents on a distribution feeder

This is a convenient method for cases where the level of the earth fault current is relatively high, i.e. directly earthed systems.

When the level of the fault current to be measured starts to decline heavily, the measurement sensitivity and accuracy that can be reached with this summation connection is no longer sufficient. The measurement accuracy is affected by the fact that the three different current transformers, even with similar core data, start to introduce different kind of errors when it comes to ratio and phase displacement.

Window-type cable current transformer
Window-type cable current transformer (photo credit: k-electric-gmbh.de)

These errors are summated together in the summation connection, and in the worst case they are cascading on top of each other. The sensitivity is affected by the fact that current transforming ratio of the phase current transformers is mainly selected based on the maximum load currents, whereas the anticipated earth fault currents can be only some fractions of those.


To overcome the accuracy and sensitivity requirements with low (earth fault) residual currents, a cable (or busbar), also called a window-type, current transformer can be utilized. Following figure describes the installation.

Figure 1 - Typical installation of cable current transformer
Figure 1 – Typical installation of cable current transformer

In the figure above, a cable current transformer is utilized for measuring the residual (earth fault) current of an outgoing three-phase cable feeder. The CT type used is a one that can be installed even after the medium voltage power cable installation is done, by opening the bolted connections and separating the CT into two parts.

It is important to notice that the medium voltage power cable screen earthings are drawn back via the CT’s window before connecting them to the earthing bar. Similarly, it is important to notice that if a separate ‘escort earthing‘ wire is installed alongside the power cable, it may not pass through the CT’s window.

The suitable current transforming ratio of the cable current transformer is depending on the actual anticipated earth fault current levels.

As an example, the ratio of 70/1A is commonly used for earth fault protection in Finland with unearthed and resonant earthed systems. The cable current transformer can also have several ratios by utilizing different tappings in the secondary side, as shown below.

A cable CT with several ratio possibilities
Figure 3 – A cable CT with several ratio possibilities

When the earth fault protection relay is connected to a certain secondary tapping of the CT, the remaining tappings should not be shorted. This applies also to the test winding tappings. On the other hand, if the cable CT has several cores utilizing separate iron cores inside the CT, each of the cores has to either be connected to a secondary device or short-circuited and earthed.

Download Schneider Electric’s ‘Current Transformers Selection Guide’ //

Download

Reference // Distribution Automation Handbook by ABB

SEARCH: Articles, software & guides

Premium Membership

Premium membership gives you an access to specialized technical articles and extra premium content (electrical guides and software).
Get Premium Now ⚡

About Author

author-pic

Edvard Csanyi

Electrical engineer, programmer and founder of EEP. Highly specialized for design of LV high power busbar trunking (<6300A) in power substations, buildings and industry fascilities. Designing of LV/MV switchgears.Professional in AutoCAD programming and web-design.Present on

2 Comments


  1. RICHARD MOSQUEDA
    Jan 30, 2016

    A example for use in isolated electrical system is the “ Difference connection -special CT”, used for Sensitive Earth Current Protection to generator Gas Turbine.


  2. Amin
    Jan 29, 2016

    Hello,
    We have a 3 core cable in 6 kv system.
    In 6 kv switchgear for earth fault protection we use a core ballance ct in bottom of gland plate,
    Armour & shiled of this cable connected to earth in above of CT (inside of feeder) , and in transformer side (6/0.4 kv) only armour of this cable connected to earth.
    is this conne tion correct for detection of earth fault?