Centrifugal water chillers comprise a significant portion of industrial and large commercial electrical load. These machines are efficient, typically producing a cooling effect two-to-three times greater than the required energy input. Centrifugal water systems were the focus of cholorfluorocarbon (CFC) legislation in the 1980 that drove the replacement or reconditioning of many of these machines.

Successful Energy Efficiency In Using Centrifugal Water Chillers
Successful Energy Efficiency In Using Centrifugal Water Chillers Dubai World Trade Center chiller plant retrofit - 39 storey building is air conditioned using (4) four water cooled centrifugal chillers (photo credit: greentechno.com)

Opportunities still exist, however, for chiller optimization. One opportunity is to change the operational strategy of multiple chillers operating on a common chilled water header.

Typically, these machines are staged so that none are loaded beyond about 80% of their rated capacity. This strategy developed as a result of the published part-load efficiencies of the machines, which tended to produce a U-shaped efficiency curve. The curve indicated that optimal efficiency was obtained at 60%-80% of full load.

Actual measurements in industrial facilities, however, suggest that the laboratory-based efficiency curve is not representative of plant conditions.

Cooling load on a typical industrial water chiller systems is often influenced by process changes that do not correspond to a linear change in condenser water temperature. The chiller efficiency, therefore, increases with increasing cooling load so that it reaches its optimum point at about full rated capacity.

Typical chiller efficiency curve is shown as a u-shape
Typical chiller efficiency curve is shown as a u-shape

Typical chiller efficiency curve is shown as a u-shape, with maximum efficiency at 60%-80% of full load. The actual measured efficiency of chillers serving industrial loads, however, is highest at full load.

Operating three chillers at partial loads is less efficient that operating two chillers at or near their rated capacity.
Operating three chillers at partial loads is less efficient that operating two chillers at or near their rated capacity.


Successful strategies for chiller optimization

Other successful strategies for chiller optimization include //


1. Chilled water reset

This strategy involves increasing the chilled water supply temperature setpoint to match the requirements of the cooling load. Reset is often performed as part of the control routines in an automatic chiller controller.

Chilled water reset can reduce compressor power consumption by 1.5%-2% per degree!

2. Reduce condenser water temperature

Similar to raising the chilled water setpoint, reducing the condenser water temperature serves to reduce the compressor power requirements. Condenser water temperature reduction of one degree can reduce compressor power consumption by 0.5%-1%.


3. Monitor and maintain chiller approach temperatures

Chiller condensers and evaporators are shell-and-tube heat exchangers that require periodic maintenance to maintain optimum heat transfer characteristics. Since water travels through the condenser and evaporator tubes, solids have a tendency to accumulate on internal tube surfaces, requiring annual “rodding” to remove the scale and restore heat transfer coefficients.

Annual average readings of condenser approach temperature
Annual average readings of condenser approach temperature

Annual average readings of condenser approach temperature (difference in temperature between condenser water and refrigerant in shell-and-tube heat exchanger) gradually crept up from the initial design value of 6 F to nearly 15 F over three years.

Increase in condenser tube fouling
Increase in condenser tube fouling

Increase in condenser tube fouling can have a significant adverse effect on compressor power consumption.


Heating, ventilating, and air conditioning systems

HVAC systems should be the focus of a targeted energy study, with similar objectives as the lighting analysis //

  1. Turn off unnecessary HVAC equipment during unoccupied times
  2. Match HVAC operation, including temperature and humidity, to minimum occupancy requirements
  3. Replace inefficient HVAC systems and equipment with energy-saving alternatives

Water Cooled Condenser Centrifugal Chiller


Water Chiller Carrier


Reference // Electrical Energy Management – Bill Brown, P.E., Square D Engineering Services

SEARCH: Articles, software & guides

Premium Membership

Premium membership gives you an access to specialized technical articles and extra premium content (electrical guides and software).
Get Premium Now ⚡

About Author

author-pic

Edvard Csanyi

Electrical engineer, programmer and founder of EEP. Highly specialized for design of LV high power busbar trunking (<6300A) in power substations, buildings and industry fascilities. Designing of LV/MV switchgears.Professional in AutoCAD programming and web-design.Present on

Leave a Comment

Tell us what you're thinking... we care about your opinion!

Premium Membership

Get access to premium electrical guides, technical articles and much more!