Calculation of the energy savings
In order to calculate power factor correction for your installation, your should follow the steps below:
Step 1 – Calculate Actual Load (kW)
(Load) Power kW = Volts V x √3 x Current I x Power factor Pf
Step 2 – Calculate Required Power Factor Correction (kVAr)
Power Factor Correction kVAr = Power kW (TanΦi – TanΦd)
Φi = Cos-1 Initial Power Factor Pf
Φd = Cos-1 Required Power Factor Pf
Step 3 – Calculate Actual Power Factor Correction [kAVrl
Actual Power Factor Correction Pf = Cos (Tan-1 (TanΦiCorrection kVAr/Power kW ))
Typical Power Factor Correction available in multiples of 25kVAR’s, for further details please Contact Blakley Electrics Technical Department.
At the end of the spreadsheet you will get the calculation of the energy savings for above power factor correction.
  1. Initial Current (Amps)
  2. Original Load (kVA)
  3. Corrected Current (Amps)
  4. Corrected Load (kVA)
  5. Reduction in Current (Amps)
  6. Reduction in Load (kVA)
  7. Annual CO2 Savings ( kg C02)
Software:Power Factor Correction Calculation
Version:
Developer:Blakley Electrics
Price:Free
Power Factor Correction Calculation Spreadsheet
10 Comments
  1. bvenu
    Oct 05, 2015
    sir i am working as a technician in private industry, plant is running with load about 900 kva how much capacitance we should need to connect, what kind of problems arise when we are connect capacitance more than required value kindly send the answer to my mail id
    thanking you sir.
  2. nirnal kumar
    Aug 07, 2015
    sir, give me formula for improve power factor. how can i get which capacitor will improve power fsctor
  3. eng.saif.
    May 17, 2015
    thanks a lot for sharing of important electrical information .I thinks this side is very helpful for EEE ,MEE,
  4. ghasem razeghi
    Mar 09, 2015
    I am an electrical engineer graduated from s.j.c.e mysore – india .
    good information i got from your site.
    thanks a lot.
  5. Revocatus Mwankemwa
    Jan 10, 2015
    The information I have got are very useful and are of great importance to the problem that I was working on.
  6. Kalim Rahman
    Nov 11, 2014
    How to find out the wire size for connecting to PFI unit?? We have an 800kva substation.
  7. Santanu Mukherjee
    Dec 21, 2013
    Thanks for sharing such nice information
  8. Engr Khan
    Nov 04, 2013
    Thanks for sharing such nice information…. but i want to add some basic formulas
    fromHow to Calculate the Suitable Capacitor Size in Farads & kVAR for Power factor Improvement (Easiest way ever)