Plant protection system functional testing

Protective circuit functional testing, including lockout relay testing, must take place immediately upon installation, every 2 years thereafter, and upon any change in wiring.

Operation, maintenance, and field test procedures for protective relays and associated circuits
Operation, maintenance, and field test procedures for protective relays and associated circuits (photo credit: Omicron)

If applicable, documentation is required detailing how verified protection segments overlap to ensure there is not a gap when testing the total protection system.

The protection circuits include all low-voltage devices and wiring connected to: instrument transformer secondaries, telecommunication systems, auxiliary relays and devices, lockout relays, and trip coils of circuit breakers.

Protection circuits also may include all indicators, meters, annunciators, and input devices such as governors, exciters, and gate closure control circuits if required for the correct function of the protection system.

Although testing of individual components may take place on a regular basis (e.g., relay calibration and lockout relay testing), it is essential to test the entire protection circuit, including wiring, and all connections from “beginning to end” to ensure integrity of the total circuit.

Critical examples of these circuits include, but are not limited to, the generator protection (86G), generator differential protection (86GD), transformer differential protection (86KD), and unit breaker failure protection (86JF) circuits. See the block diagram, figure 1.

Total plant protection system functional testing block diagram
Figure 1 – Total plant protection system functional testing block diagram (click to expand block diagram)

Primary and secondary injection test techniques

One approach to test the total protection system is to use primary injection techniques (see appendix H) that trigger protective relays and lockout relay, trip circuit breakers, and initiate annunciations and indications.

This technique also tests the CT or PT ratios, polarity, and phasing. Verify PT and CT secondary grounding in separate tests. If primary injection is not possible, use secondary injection techniques.

These techniques locate wiring errors, insulation failures, loose connections, and other problems that go undetected if only relays are tested. Test each part of the entire system at least one time. For example, on a three-phase overcurrent relay, it would be necessary to inject a current at the phase A CT and verify that the relay and associated breaker trip.

The phase B and C CT also would need to be tested in a similar manner; but the trip lead from the relay may be lifted, since this part of the circuit already was tested.

Title: Operation, maintenance, and field test procedures for protective relays and associated circuits – U.S. Department of the Interior Bureau of Reclamation Denver, Colorado
Format: PDF
Size: 1.7 MB
Pages: 123
Download: Right here | Get Download Updates | Get Premium Membership
Operation, maintenance, and field test procedures for protective relays and associated circuits - U.S. Department of the Interior Bureau of Reclamation Denver, Colorado
Operation, maintenance, and field test procedures for protective relays and associated circuits – U.S. Department of the Interior Bureau of Reclamation Denver, Colorado

Premium Membership

Premium membership gives you an access to specialized technical articles and extra premium content (electrical guides and software).
More Information

Leave a Comment

You must be logged in to post a comment.

Login

Subscribe to Weekly Digest

Get email alert whenever we publish electrical guides and articles.