Fundamental features
Distance functions have been in use for many years and have progressed from the original electromechanical types through analog types and now up to digital types of functions.
The purpose of this paper is to discuss fundamental features of the three types of functions and possible problems that may be encountered in their design and application.
Simple MHO Function
A simple mho distance function, with a reach of Z ohms, is shown in Figure 1. This diagram is exactly equal to an R-X diagram except that all of the impedance vectors have been operated on by the current I. The mho function uses the current and voltage measured at the relay to determine if the apparent impedance plots within the mho characteristic.
The determination is made by comparing the angle between the operating quantity (IZ – V) and the polarizing quantity (V, where V = IZf). If the angle is less than or equal to 90¡, then the fault impedance Zf plots within the characteristic, and the function will produce an output. If the angle is greater than 90¡, then Zf falls outside of the characteristic and no output will be produced. Assume that the angle of maximum reach (q) and the angle of ZL (f) are equal. On that basis, the conditions shown in Figure 2 will be obtained. The key point to note in this phasor analysis (a convenient way to view relay performance) is the magnitude of the IZ – V (Vop) phasor and its relationship to the V (Vpol) phasor.
Operation will occur whenever Vop and Vpol phasors are within 90¡ of each other and provided both Vop and Vpol are greater than the minimum values established by the sensitivity of the relay design.
Title:Distance Relay Fundamentals
  1. Rick Willet
    Jun 17, 2015
    Could not download any of the guides.
      Maybe it’s some glitch at the Box side, file is downloadable, I just checked.
  2. cuami
    Apr 07, 2013
    Anyone having soft copy of “Numerical distance protection by gerhard ziegler” please share it. Thanks