Technical Considerations in the Specification and Design of Low-Voltage Switchboards (photo by: deltatherm.de)
Switchgear access
Cubicles may be front access only, rear access only or front and rear access. This has clear ramifications with regard to cable accommodation and access.
What should not be overlooked with the Front access only configuration, is the fact that rear access may be available during the factory build period and that components – such as fuses, CT’s etc, are located such that they can be accessed when installed on site and in service.
Forms of Separation
This essential aspect of switchboard design deals with the separation of live parts, functional units, terminals and glanding facilities and is defined in BS EN 60439.
Low-voltage switchgear - Types of forms of separation
Low-voltage switchgear – Types of forms of separation
Detailed information is also available in the BEAMA Installations’ “Guide to Forms of Separation”.
Fault Rating/Fault Level
A typical specification requirement where the supply is derived from transformer/s up to 2 MVA would be 50KA RMS sym 1 sec.
Specifiers often state a fault rating of equipment considerably above that which can arise in the system – this is their prerogative. Sometimes however, there is “more behind this” – the consideration of other power sources, which may parallel with the system – and a little known subject – motor contribution.
CASE: If a load has a large motor content this may become a source of regenerated energy during a short circuit fault on the system. The effect is that certain sections of the switchboard busbars have to carry the fault current “expected” from the supply source plus the regenerated (reverse current) from the rotating machines.
Fault rating or fault withstand capability is a safety statement that the equipment or device can without hazard to personnel, or equipment damage, operate or be operated up to that fault level and be suitable thereafter for further service, albeit in some cases at reduced load level.
In order to appreciate what has to be considered in the selection of components and the design of equipment to cater for the above requirements, it helps to have an understanding of what happens during a fault current transient period and the terminology used.
The following illustration graphically shows a typical short circuit current transient:
Relationship between RMS symmetric short circuit current, power factor and asymmetric peak current to RMS symmetric current multiplier, n
When a short circuit fault commences, an asymmetrical condition of the waveform initially occurs. A DC component, proportional to the fault circuit power factor effectively raises the sine wave zero axis thereby increasing the Peak Value of the current wave relative to the original axis during the first few cycles.
The “normal” peak value (if the wave is sinusoidal and symmetrical) will be
1.414 x the RMS value.
As can be seen from above illustration, the low power factor of the fault circuit (not to be confused with the distribution system PF) brings about an increase @ 0.25 PF to 2.1 x RMS.