Substation Design Guideliness
Substation Design Guideliness (photo credit: vaughnindustries.com)
Consider open loop MV network as an example
The rating of substation equipment as well as the connections must be decided.
Detail design of substation
Selection of substation equipment
Switchgear
  1. Selection of transformers
  2. Ratings of circuit breakers
  3. Ratings of switch disconnecters (Load-break switches)
  4. Ratings of isolators (Disconnecters)
Measurement
  1. Characteristics of voltage transformers (VTs)
  2. Characteristics of current transformers (CTs)
Selection of Transformers
  1. Transformer size/s must be selected according to the maximum expected load and possibility of future expansions.
  2. The size of transformer may be selected from power ratings given below to supply present and future loads.
Commonly available ratings for substation transformers
Rated powers:
25 kVA, 50 kVA, 100 kVA, 250 kVA, 400 kVA, 630 kVA, 800 kVA, 1000 kVA, 1250 kVA, 1600 kVA, 2000 kVA
Primary voltages (line-to-line):
6 kV, 7.2 kV, 10 kV, 12 kV, 22 kV, 24 kV, 31.5 kV, 33 kV, 34.5 kV, 35 kV, 36 kV
Secondary voltages (line-to-line): 380 V, 400 V
Example:
Substation Design
Consider that you would like to choose a transformer to supply power to a factory which requires maximum of 270 kVA of power at 400 V on the LV side and no expension is considered for near future.
The power will be provided by connecting the factory to 33 kV MV voltage level. Choose the transformer.
Solution:
Powers:
Primary Voltages (line-to-line): 6 kV, 7.2 kV, 10 kV, 12 kV, 22 kV, 24 kV, 31.5 kV, 33 kV, 34.5 kV, 35 kV, 36 kV
Secondary Voltages (line-to-line): 380 V, 400 V
Selected transformer size for the factory:
400 kVA, 33 kV/400 V
Title: Substation Design Guideliness – Schneider Electric
Format: PDF
Pages: 40
  1. Subodha Ranaweera
    Jan 13, 2015
    Can i have the design details of closed ring operated MV network?
  2. SWBD APPEARS TO BE INDOOR. TRNS CAN NOT BE OIL OR AN EXPENSIVE VAULT WILL BE REQUIRED IF IS LOAD CENTER THE TFRM WILL HAVE TO BE DRY, DIFFERENT TYPES,. ASSUMED THE SYSTEM FREQUENCY IS 50 HERTZ. IF DRAW OUT BREAKERS
    ASSUMED NOT POWER BREAKERS, PROBABLY INSULATED CASE. A DECISION WILL HAVE TO BE MADE FOR THE CLEARANCE IN FRONT OF THE SWITCHBOARDS. INDICATE UNITS, METRIC, OR ENGLISH TO ESTABLISH IF THE COUNTRY HAVE AN ELECTRICAL CODE.I ILL STOP HEAR.
    THANKS AND REGARDS