Personal Protective Grounding for Electric Power Facilities and Power Lines
Instructions and procedures
This Facilities Instructions, Standards, and Techniques (FIST) Volume is to establish clear and consistent instructions and procedures for temporary grounding of deenergized and isolated high-voltage equipment (over 600 volts) for the purpose of bare hand contact.
This FIST applies to those facilities of the FEederal power and water systems for which the Bureau of Reclamation (Reclamation) and its contractors and agents are responsible, and includes power and pumping plants, switchyards and substations, and transmission lines.
Scope
These instructions and procedures supplement the requirements in Reclamation Safety and Health Standards, “yellow book”. Adherence to these procedures will enable workers to perform their duties with maximum confidence and safety.
In the event of a difference between the requirements in this FIST and those contained in the Reclamation Safety and Health Standard, the more rigorous requirement shall apply.
The primary purpose of personal protective grounding is to provide adequate protection against electrical shock causing death or injury to personnel while working on de-energized lines or equipment.
This is accomplished by grounding and bonding lines and equipment to limit the body contact or exposure voltages at the worksite to a safe value if the lines or equipment are accidentally energized from any source of hazardous energy.
The greatest source of hazardous energy in most cases is direct energization of lines or equipment from the power system.
Other sources of hazardous energy may include:
  1. Stored energy (capacitors)
  2. Static build-up
  3. Faulted equipment
  4. Electromagnetic coupling
  5. High-voltage testing
  6. Instrument transformer
  7. Back-feed
Title:Personal Protective Grounding for Electric Power Facilities and Power Lines – U.S. Department of the Interior; Bureau of Reclamation; Denver, Colorado
Pages:89
  1. DERLY FOSTING
    Oct 27, 2013
    Wao… Excelente el aporte Muchas gracias
  2. semens
    Oct 26, 2013
    please answer
    why i can,t download
      Edvard
      Oct 26, 2013
      Are you registered member of EEP? If not, go ahead and register, it’s free ;)