Search

Premium Membership

Get access to premium HV/MV/LV technical articles, electrical guides, research studies and much more! Get 20% OFF Code: EEP08PR
Home / Technical Articles / Control house at HV/EHV switchyards and substations (construction, layout and functions)

Control house

Nowadays, the control house is one of the main parts in every modern HV switchyard and substation. Why? Simply, because substations have grown in complexity and equipment such as circuit breakers, switch disconnectors, CT, VTs and others must be controlled, monitored and protected from some common point in the field.

Control house at HV/EHV switchyards and substations (construction, layout and functions)
Control house at HV/EHV switchyards and substations (construction, layout and functions) - photo credit: eq-house.com

Necessity for supplemental equipment such as protection relays, controls, batteries, communications equipment, and LV distribution equipment also increases. And all that equipment must be placed somewhere in the field.

That’s why substation needs a control house. In short.

For small distribution substations, this equipment can usually be contained in weatherproof enclosures or control cabinets. For larger substations, separate equipment housing is necessary.

A control house provides a weatherproof and, if required, environmentally controlled enclosure for supplemental substation equipment. Additional space can be provided for workshops, equipment testing and repair, storage areas, and lavatory facilities.

MV and LV switchgear can also be contained within control houses, or this equipment may be contained within weatherproof enclosures dedicated to that purpose.

Location of control house in power substation
Figure 1 – Location of control house in power substation

Contents:

  1. Control house construction:
    1. Foundation
    2. Floor
    3. Control house structure
  2. Control house layout:
    1. Control and relay protection panels
    2. DC equipment
    3. AC equipment
    4. Cableways
    5. Cable entrance
    6. Lighting
    7. Control house HVAC systems
    8. Control house plumbing
    9. Communications

1. Control house construction

This section discusses general aspects of the control house construction.

1.1 Foundation

The control house foundation typically consists of a spread footing with either masonry blocks or cast-inplace walls. The footing is designed for an allowable bearing capacity based on soil data. If soil data is not available, a maximum bearing of 48 kPa can be used.

The footings are installed below frost depth and in accordance with local building codes and practices.

Drilled piers are an alternative to spread footings. Drilled piers are especially applicable for pre-engineered metal buildings with structural supporting bases that can rest directly on the piers without requiring a concrete floor slab. Soil data is necessary for determining the required depth, diameter, and reinforcing of the piers.

Damp-proofing of foundation walls is desirable, especially if concrete block is used. If a basement level is constructed, damp-proofing should be provided.

Footing drains are usually provided when a basement level is constructed. All foundation walls should be insulated with a 5.1-cm (2-inch) thickness of rigid insulation for energy conservation.

It is preferable to install the insulation on the inside of the walls, although the outside is acceptable.

New control house piers poured and cables installed before the control house arrives
Figure 2 – New control house piers poured and cables installed before the control house arrives

Go back to contents ↑

1.2 Floor

The control house floor is typically a floating concrete slab 12 to 16 cm thick reinforced with welded wire fabric, deformed steel bars, or a combination of both.

The finished floor elevation is usually 10 to 20 cm above the finished grade outside the control house.

The base beneath the floor slab should be 10-12 cm of compacted sand or gravel, thoroughly mixed and compacted sand or gravel, or thoroughly mixed and compacted natural soil. A 0.15 mm thick plastic film vapor barrier should be installed between the floor slab and the base.

The method for cable routing in the control house has to be considered before finalization of the floor slab design. Cable trenches can be formed into the floor slab, or false floors can be installed providing access to large areas below the finished floor.

Go back to contents ↑


1.3 Control house structure

The control house structure must be constructed from fire-resistant, low-maintenance building materials. Most control houses presently being designed and constructed are of the pre-engineered metal or masonry block type.

Figure 3 show example of control building structure type.

The pre-engineered metal building is the easiest to procure and erect. The manufacturer can design and fabricate the required building components when given the building size; wind, snow, and ice loads; and any special requirements such as additional roof loads for suspended cable trays or other equipment.

Masonry buildings constructed of block masonry are most economical when masonry module dimensions are used to size the building and the building openings.

Switchyard control house construction, layout and functions
Figure 3 – Control house on the left

Two types of roof systems are commonly used for masonry buildings: pre-cast, pre-stressed concrete panels; and steel joists and steel decks. A sloping roof is recommended for both systems and can be obtained by pitching the roof deck or installing tapered roof insulation.

The roof membrane has to be compatible with the slope. For the slopes of 8.3 cm/m (1 in./ft) and less, built-up pitch and slab is commonly used. For greater slopes, gravel is used.

The control house should be equipped with at least one double door, possibly with a removable transom, conveniently located to facilitate equipment entry and removal. In certain circumstances a second exit needs to be installed in the control house.

The National Electrical Safety Code (NESC) states:

If the plan of the room or space and the character and arrangement of equipment are such that an accident would be likely to close or make inaccessible a single exit, a second exit shall be provided.

The National Electrical Code (NEC) also defines specific requirements for a second exit. The doors should include locking devices, astragals to prevent water from entering, and adequate weatherstripping and hardware to permit a rapid exit from the control house.

Adequately ventilate the battery area, either by a natural or powered ventilation system, to limit accumulation of hydrogen gas to less than an explosive mixture. A powered ventilation system needs to be annunciated to indicate ventilation failure. Provide portable or stationary water facilities or a neutralizing agent for rinsing eyes and skin in the battery area in addition to proper eye protection and clothing.

Locate and mark adequate fire-extinguishing equipment in the control house. Windows can be provided, if desired, in office and lavatory areas. Battery rooms and control and metering areas do not need windows.

Consider adequate methods for building insulation. These methods include use of insulated wall panels, ceiling insulation, storm doors, and windows, and weatherstripping around all openings.

Metal buildings are shop painted and require only minor field touch-up after erection. Masonry buildings may be left unpainted or may be painted with portland cement or latex paint. Tint all prime coats to match the finished coat.

Go back to contents ↑


2. Control house layout

2.1 Control and Relay protection Panels

Most protection relaying, metering, and control equipment is mounted on fabricated control and relay panels installed within the control house. A variety of panel types is available to suit individual requirements.

Figures 4, 5 and 6 show examples of various panel layouts.

Control and protection panels
Figure 4 – Control and protection panels

Single vertical panels can be used, particularly for distribution circuits where space requirements are minimal. The relaying, metering, and control equipment can all be mounted on one panel, allocating a separate panel for each circuit. In some instances, two circuits may share the same panel.

Double or duplex panels are commonly used for higher voltage circuits, necessitating additional space for equipment mounting. Normally, these panels are arranged in two parallel rows with the panel backs facing each other. In this configuration, operating, instrumentation, and control equipment for a circuit is installed on the front of one panel, and the corresponding relaying equipment for the same circuit is installed on the front of the panel directly to the rear.

Protection relay panel
Figure 5 – Protection relay panel (photo credit: pestech.com.my)

In some instances, two circuits may share the same control and relaying panels.

Some equipment such as static relaying systems and communications equipment is available mounted in racks. Consequently, separate relay and/or control panels are not required for this equipment.

Modern SCADA and substation automation schemes may require space for installation of a PC with monitor and keyboard, as well as programmable logic controllers and data highway interface modules. This equipment can often be rack-mounted or installed in control panels, as appropriate.

The trend is toward more compact equipment arrangements that often reduce overall control house size.

Individual three-phase microprocessor relays can replace three single-phase electromechanical relays and associated voltage, current, and power meters, all in one case.

Compact relay and programmable logic controller designs can be mounted on 48.26-cm (19-inch) racks.

Relay protection panels in control room
Figure 6 – Relay protection panels in control room (photo credit: Protection Installation Services Ltd)

To facilitate operation, panels are located in an arrangement that conforms as closely as possible to the actual equipment and circuit layout in the substation yard. To assist in circuit location and operation, mimic buses are sometimes used on the control panels, particularly for large complex substations.

The mimic buses identify the bus and circuit arrangements.

Mimic diagram in protection relay panel
Figure 7 – Mimic diagram in protection relay panel (photo credit: Edvard Csanyi)

Mimic buses may be implemented on screens viewed from a PC monitor. When practical, position meters at eye level and switches at a convenient operating level. Locate recording meters for ease of viewing and chart replacement.

Locate relays beginning at the tops of the relay panels and working downward. Relays with glass covers should not be located within 12 inches of the floor to avoid inadvertent breaking of the glass. Locate operating switches at convenient heights near the center of the boards. Require nameplates for all devices.

Provide ample space for relay installation, removal, operation, and testing. Panel construction can include removable front plates for device mounting.

Panels may also include 19-inch rack mounting facilities. Many of the newer relays and items of accessory equipment are designed to fit into 19-inch racks. Cover plates may cover space reserved for future use. In this way, only a new predrilled plate is required when changing out a device or modifying the configuration.

Cutting, drilling, or covering openings in the panels is eliminated.

19-inch rack-mounted protection relay, type MICOM
Figure 8 – 19-inch rack-mounted protection relay type MICOM and test sockets (photo credit: Edvard Csanyi)

Panel wiring is accomplished on the backs of the panels. Devices are interconnected and wired to terminal blocks, as required, for operation and connection to devices on other panels.

Panels can include small sections perpendicular to the main section at each end for installation of terminal blocks, fuse blocks, or small auxiliary devices.

Cable connections from the equipment in the substation yard can be made directly to terminal blocks mounted on the panels or to strategically placed terminal cabinets. Interconnections between the terminal cabinets and the panels can then be made with single conductor wire.

Cabling of relay protection panels
Figure 9 – Cabling of relay protection panels

Anchor panels to the floor in such a way as to facilitate relocation to coincide with yard equipment and circuit relocations.

Panel arrangement in the control house should permit ready accessibility to the backs of the panels. Some vendors of pre-engineered buildings can provide completely wired and tested control and relay panels and auxiliary AC/DC power systems as part of the building package.

In this case, custom-designed relay and control schematics are submitted to the building vendor. The building vendor fabricates the panels, provides the relays and controls, wires the panels, and tests the complete installation.

In this way, the entire panel line-up can be witness-tested in the factory. The complete building system is shipped to the site, fully tested. Only the external wiring from the building to the outdoor equipment has to be field-installed.

Go back to contents ↑


2.2 DC Equipment

Substation DC equipment located in the control house normally consists of the battery, battery charger, monitoring and control devices, and distribution panelboard.

The battery should be located in a separate room where practical. If the battery cannot be located in a separate room, it should be located so that electrical switching devices and receptacles are not in the immediate vicinity, ventilation is adequate to prevent gas accumulation, and live parts are protected from accidental contact.

The battery charger, monitoring and control devices, and distribution panelboard are normally located in the control and relay room to facilitate cable routing and equipment maintenance.

Detailed design requirements and procedures for the substation DC system can be found in this technical article.

Left: Battery room; right: Battery chargers
Figure 10 – Left: Battery room; right: Battery chargers

Go back to contents ↑


2.3 AC Equipment

A low-voltage AC system is provided in the substation for lighting, convenience outlets, heating, ventilating, air conditioning (HVAC) equipment and miscellaneous control functions.

Convenience outlets should be strategically located throughout the control house to provide adequate accessibility. Also, if necessary, workshop and testing area with a high-capacity AC source and a three-phase source should be provided.

For greater reliability, two separate sources may be provided for the AC system service. These sources are often fed through a manual or automatic transfer switch so that ac system power can be restored if one source fails.

Substation AC Auxiliary Supply For Inessential Loads
Figure 11 – Substation AC Auxiliary Supply For Inessential Loads (on photo: AC auxiliary switchgear 400/230 V; credit: ZPAS Group – zpasgroup.co.uk)

Go back to contents ↑


2.4 Cableways

Cable routing can be accomplished by using any of several methods.


2.4.1 Cable Trenches

Cable trenches are formed into the concrete floor slab and are covered with metal plates. The covers should be flush with the finished floor when in place.

The sizes and locations of the cable trenches are based on the quantities of cables and locations of panels and equipment to be interconnected. Usually, a cable trench is located adjacent to the backs of the control and relay panels to facilitate panel interconnections.

With duplex panels, it may be desirable to use the entire space between the front and rear panels as cable trench, depending on circuit quantities.

Concrete cable trenches in control house
Figure 12 – Concrete cable trenches in control house

Go back to contents ↑


2.4.2 False Floors

False floors are useful when large open areas are desirable for cable routing. Lightweight removable floor panels installed on adjustable pedestals are positioned in areas requiring extensive cable interconnections or where future plans dictate a large amount of cable rerouting.

The top of the removable panels should be flush with the finished floor.

When cables are mounted under false floors, establish routes and paths in which cables should be routed. This will allow the separation of circuits as required to maintain system reliability based on duplicate circuits.

If circuits in one area are damaged, other undamaged circuits in the other parts of the building are likely to keep the substation in service.

Go back to contents ↑


2.4.3 Conduits

Conduits can be used for cable routing in floors, along walls, and for cable entrance into the control house. Conduits are available in plastic, aluminum, and steel. Each of these types may be used in control houses for wire containment to convenience outlets, lighting fixtures, and other control house auxiliary power equipment.

Plastic conduit is easily installed and is available in a variety of sizes. Take adequate physical and thermal precautions when using plastic conduit to ensure safe operation.

Metallic conduits of aluminum and steel are widely used as control house cableways. Intermediate- and heavy-walled steel conduit provide excellent physical protection.

Cables in false floor of a substation control house
Figure 13 – Cables in false floor of a substation control house

The installed costs, however, may be relatively high because of the extensive labor required for installation. The installed cost of rigid aluminum conduit may be somewhat less than that for steel.

A lower installed cost may be realized by using thin-walled steel conduit (i.e., electrical metallic tubing) since it is less expensive and easier to install.

Go back to contents ↑


2.4.4 Wireways

Wireways are sheet-metal troughs used for routing groups of power circuits around a control house to feed various branch circuits. Conduit is used between the wireway and the devices.

Wireway offers the advantage of laying rather than pulling the cable into position and the ability to change or reroute circuits easily. Wireway is available with hinged or removable covers in a variety of lengths and sizes.

Select and install wireway in accordance with the National Electrical Code.

Cables laid on metallic wireways in false floor
Figure 14 – Cables laid on metallic wireways in false floor

Go back to contents ↑


2.4.5 Cable Trays

Cable trays can be used for overhead routing of cables to and between control and relay panels. Expanded metal or ladder-type trays provide the best facilities for conductors entering and leaving the trays.

An advantage of cable trays is the ability to lay rather than pull in the conductors. Suspended cable trays, however, prevent extensive use of this technique because of support locations.

A large variety of types, sizes, and fittings is available to suit individual requirements. Cable tray should be selected and installed in accordance with the NEC and NEMA Standards.

Cables in trays entering panels
Figure 15 – Cables in trays entering panels

Go back to contents ↑


2.5 Cable Entrance

Control and power cables are brought into the control house through windows, sleeves, or cable pits. The windows are square or rectangular openings, usually through the foundation wall but possibly above grade.

The window openings enable many cables to be pulled without interference. To protect the cables during pulling, the windows should have smooth surfaces and beveled or rounded edges. After cable pulling, split sleeves can be installed around the cables and grouted into place.

Occasionally, the windows are left open to facilitate future cable installation. Heat loss through these openings should be considered. Provide additional windows for installation of future cables. The windows can be constructed and bricked up to be opened when required.

Cable sleeves can be used above or below grade. The sleeves are usually cast into place during construction of the foundation wall or installed during construction of the superstructure.

Pitch the sleeves to drain out of the building. Provide covers over the cables. Install spare sleeves during initial construction.

Cable pits may be cast-in-place concrete or masonry openings through the control house foundation to permit access to the inside at floor level. Install a cover over the pit and provide a means to drain water.

Cables entries in control house
Figure 16 – Cables entries in control house

Go back to contents ↑


2.6 Lighting

Fluorescent lamps are generally used for lighting in control houses. The trend is toward energy-saving lamps and energy-saving electromagnetic or electronic ballasts.

Install lighting to eliminate, as much as possible, reflection and glare from meters, relays, and monitoring screens.

An emergency DC-operated incandescent system is recommended for most control houses. This system can be operated in case of failure of the ac system. It can be operated from battery-pack units or from the station battery system.

Go back to contents ↑


2.7 Control House HVAC Systems

To maintain the functions and accuracy of electrical equipment installed in the control house, HVAC systems may be desirable.

In areas requiring heat only, unit electric space heaters are positioned throughout the control house for balanced heating. If both heating and cooling are required, electric heat pumps can be used. Several small units, or one large unit with a duct system for air distribution, can be used. Supplemental electric resistance heating coils may be required for heating in colder areas.

In some cases baseboard radiation heating units can be used in rooms not reached by the main heating system. These rooms include offices, lavatories, and storage rooms.

The battery room is sometimes left unheated. However, maintenance of battery temperature close to 32°C will prolong the life and capacity of most battery systems.

Temperature control levels may vary because of several requirements. Operating ranges of equipment have to be considered as well as economics. It is recommended that consideration be given to a dual control.

Louvers to achieve good air circulation
Figure 17 – Louvers to achieve good air circulation

Most stations will be unattended and, therefore, a normal personal comfort level is not required. However, for maintenance reasons, comfort levels are necessary.

If the control house is to be heated only, it is usually desirable to install power ventilation equipment for air circulation. Size the system for three to five air changes per hour. Place power-operated, thermostatically controlled roof ventilators and manually operated wall louvers to achieve good air circulation.

Position wall louvers so that equipment does not interfere with air circulation. Provide fusible links to close the louvers in case of fire.

It is advisable to provide ventilation that will maintain a positive pressure within the control house at all times to prevent dust from entering through doors and other openings, and prevent accumulation of combustible gases.

If control house air conditioning is used to provide positive air pressure, then the vent should remain open and fan should run continuously. This also applies if the unit is a heat pump.

The isolated battery room should be equipped with a gravity roof ventilator to remove corrosive and combustible gases. Do not use power-operated roof ventilators.

Go back to contents ↑


2.8 Control House Plumbing

Control houses may require plumbing for stationary eyewash facilities. Additionally, very large, major locations may warrant a shower, lavatory, drinking fountain, and maintenance sink.

A water supply, when required, may be obtained from an existing system or a private well on the substation site.

Most substations with toilet facilities will require septic tank and drain field systems.

Go back to contents ↑


2.9 Communications

A commercial telephone is usually installed in the control house for external communications. Additionally, system telephones or voice channels over carrier systems may be used for system communications.

Larger installations may include substation automation systems or SCADA for remote control and monitoring of substation equipment.

Go back to contents ↑


References:

  1. Design Guide for Rural Substations by United States Department of Agriculture
  2. Drop-In Control House for a Large 230 kV Transmission Substation: A Case Study in Implementation by Douglas M. Arcure (Shaw Group) and Chris Clippinger (Schweitzer Engineering Laboratories, Inc.)

Premium Membership

Premium membership gives you an access to specialized technical articles and extra premium content (electrical guides and software).
Get Premium Now ⚡
author-pic

Edvard Csanyi

Electrical engineer, programmer and founder of EEP. Highly specialized for design of LV/MV switchgears and LV high power busbar trunking (<6300A) in power substations, commercial buildings and industry fascilities. Professional in AutoCAD programming.

2 Comments


  1. Sk samirul hoque
    Mar 19, 2019

    Hi sir,
    I am SK samirul hoque, I have completed electrical engineering (B-Tech) from India, I need to practical knowledge about the electrical construction side, ( MV/LV substation, panel wiring, MCC, Switchgear system, Electrical control system, testing and commissioning, etc , please give me suggestion what is better way for me,
    Thank you sir for your Care for us ,,,


  2. Prince Clark
    Mar 11, 2019

    Hi, I am Prince K. Clark, from Liberia.
    I studied electrical engineering. I love presentation. I need a serious practice.

    I really want to be in contact with you please.
    Thanks.

Leave a Comment

You must be logged in to post a comment.

Login

Subscribe to Weekly Digest

Get email alert whenever we publish electrical guides and articles.